Trouble shooting install with solaredge optis question.

Advice Wtd / Project

Not sure if this is quite the right place to get this answered but I couldn't find an active sub that was more specific.

I was installing a rail system today with solaredge optis. After completing a section we will test the home runs to ensure everything got plugged in right. Solaredge optis will output 1v per opti in the string in their pre-commissioning mode. If it tests out v=# of optis you know its all good. If v=0 you know an opti to opti or opti to HR connection was missed. if v=# of optis - x you know that x opti to panel connection was missed.

I tested one string and v was one low. Tracking down where the missed connection is a pain in the ass on rail systems since you can't see most of them from outside the array and have to pull up each panel to check until you find it, often ruining your wire management in the process. So I had an idea.

I thought if I can cover the panel and stop the sunlight it should cause the reading to drop. I can do that to each panel until I find the one where the reading doesn't drop and than I know the problem is with that panel. This way I can avoid pulling all the other panels up searching for it.

So I got the cardboard from the pallet of panels and used it to cover a panel I know is connected correctly to test the idea. But the reading didn't drop. Why isn't this method working? Does enough sunlight make it through cardboard to still power the panel? Does the voltage differential in the panel take a while to dissipate in this pre commissioning mode?

Posted Jun 28, 2023, 9:32 PM UTC