House does not Cool Down
Afternoon All,
With the temps increasing I have noticed my house only cools down ~10 - 15 degrees from the outside. I have a Lennox 2.5 ton unit (HSXA12-030-230-01) with a TXV. I have cleaned the EVAP and Condenser coil and installed a new filter. I grab the following temps and pressures after running the system for 15 mins:
Refrigerant: R410A
Outside Temp: 28.1 C
High Side:
268.5 PSI = 31.3 C
29.0 C Line
Low Side:
92.5 PSI = -2.4 C
19.0 C Line
This to me seems like low refrigerant. Is this a correct assumption? Thanks for the help!