Circuit Board question

As I'm sure many people on here - new home owner here. Was in the process of reviewing my home with the heat pump installer, when we came across a potential issue. According to the installer - the electric circuit board is currently set up with the 200amp switch, however the wires running into it, do not match and only are rated for 100 amp load. I can see how that would be a concern as it is not up to the code and a fire hazard shall I ever overload my grid. Not to mention that it renders the 200 amp breaker pretty much useless, as I don't see how I can ever trip it.

I probably would've never questioned the installer's statement, but I clearly remember that during the home inspection (and in his report) there was never a mention of this (and the guy was VERY thorough). We also have a copy of the permit, that previous tenants had filed with the city to upgrade the current circuit and the board. The city would've scheduled an inspection after the work was completed and would've failed it, if there were code issues.

I was able to spot the writing on the wire and googled around. If my google-fu is still strong I have an aluminum 2 wire, which is, in fact only rated to 100 amps.

I am definitely not an electrician, so I was hoping that someone here with a little more knowledge can confirm? I have a few pictures that I took of the breaker and wiring here [Link to Album].

The writing on the wires are as follows:

Southwire E30117 (UL) AWG 2 (33,625 mm2) Compact AL AlmaFlex (TM) AA8176 TYP...

Thanks a lot!!

Posted Jul 31, 2014, 1:05 AM UTC

713
DocmanCC•

To correct this you have two options:

  1. Replace the 200 amp breaker with a 100 breaker. This will trip the main circuit to the house before it overloads the undersized wire, preventing a fire hazard.
  2. Replace the undersized wires with ones rated to carry 200 amp current. An electrician will need to replace the wires between your service panel and the power company meter. It may also be necessary for your power company to replace the wires going to your house from the street or utility pole. The power company will do that, but may charge you for that service.

Side note: this is a circuit board, this is a service panel, aka breaker panel, fuze box, or breaker box.

5
SoVeryAwkwardOP•

Hey. Thanks for your help. That's what the installer told me as well. It seems to me that replacing the wire would make more sense.

Do you have any idea what something like that might cost?

1
fitzwell_richard•

Electrician here. What you have there is a 200A main breaker homeline brand panel. The panel is fine is a nice one. I can tell by the looks of the wiring it was installed by a hack. No professional electrician would have left a panel looking like that. It should have failed the inspection so either the inspector doesn't know what's up or it was done under the radar. The wire is undersized, it should be 4 awg aluminum or 2 copper. Find a reputable electrician to give you an estimate to bring it up to code, tell him you'll bye the wire yourself if he gives you a length needed, you can get it at most big box hardware stores, 4-4-4-2 sc cable. Since all he has to do is pull existing wire out, pull new wire in, terminate and clean up panel it shouldn't cost more than a couple hundred bucks.

5
SoVeryAwkwardOP•

Awesome, thank you! "Roughly $500" is what I was quoted by the heat pump installer (they will provide the materials and have their own licensed electrician). The process seemed to be a little more complex for DIY from what he mentioned and consists of:

  • Getting a permit from the city
  • Power company turning off the supply
  • Swapping the wire
  • Inspection by the City
  • Power company turning the power back on.

I guess I'll wait for the official quote and probably will take your advice and see if I can find my own electrician for the task.

Once again - much appreciate your help and thorough response!

1
fitzwell_richard•

Five hundred seems on the high side. The power company doesn't charge to drop or restore power. Permit costs vary, but in this case should be a small fee. If the new wire is aluminum it runs $2.75 per foot. Copper would be around $6-$7 per foot. A job like this shouldn't take longer than two and half three hours max. Less than three hundred. Good luck.

1
Legion1107•

I concur with fitzwell. This was shotty work. Looks almost like the homeowner had a small 100a service, maybe a small 18 circuit panelboard, and decided to upgrade the panel, ignoring the service feed. My 2 cents, spend the extra on copper wire. Aluminum has to be re-torqued every so often, which most homeowners ignore and never do. $500 seems high if you are providing the material. Should take the electrician all but an hour to do the work, plus the permit process.

1
m_80•

2 gauge aluminum is indeed limited to 100 amps by code, so if there is no other 100 amp fused disconnect or breaker ahead of this panel then the main breaker should be switched to 100 amps. If there is a breaker or fuse ahead of this panel (look outside near the meter) then that 200 amp breaker in the panel isn't much of an issue because the breaker upstream will protect the wire in the event of a overload.

2
SoVeryAwkwardOP•

Cool, good to know! Thank you!

1
EyeHamKnotYew•

"Awg 2 "is the correct size identifier and "al" is aluminum. How many wires feed your main panel? 2 positive and one negative or one positive and one negative. 3 wires total equals 120/240 service and 2 wires total equals 120v service.

0
SoVeryAwkwardOP•

It seems like there are only 3 wires going into the board (positive, negative and a ground?)

1
EyeHamKnotYew•

It's 2 hot and 1 neutral. The ground goes Into the ground. I just realized you posted pictures. My bad. My guess is that the breaker panel was upgraded and the overhead or feeder lines from the street were not upgraded.

1
SoVeryAwkwardOP•

Hey! Thanks for your help! Good to know.

1