Can I run conduit through a notched 2 x3 that hangs on my exterior wall?
I'm using conduits because its code where I live, plus it's what I'm most familiar with. I recently ripped out the old plaster on rock lathe and the 1x2's in my kitchen. I will being replacing the 1x2 furring strips with 2x3's. I would notch the 2 x3's to fit 1/2 EMT. The 2x3's will be used to hang new dry wall and some cabinets.
Posted Oct 30, 2017, 4:52 PM UTC
15
As long as they're not structural and you put nailing shields over them where they're notched so you don't accidentally drywall screw into them, that should be fine.
Thanks, that's what I was thinking.
Do you need nailing shields for conduit?
I'm not sure if they're required by code for metal conduit. I believe they are for plastic conduit, and would be advisable even if not required.