r/hvacadvice•
sposda

Should I fix or replace my 1-1/2 hydronic circulator

I bought an old house last year. When the heat first kicked on last year, it overheated the first time. I oiled the pump and bearing and it worked ok all winter, maybe a little noisy. The inside of the bearing looked like a lot of dried grease and felt sorta stiff. I drained the system and took things apart to inspect.

The pump and bearing are from 1966. MOT441-6 and P7Z-4351. I don't see any visible damage to the steel impeller. It looks like one of the studs broke off the volute at some point and they tapped it instead.

Wondering if I should try to rebuild the bearing and replace the mounts, replace the bearing with a Taco BRG-B-100, or replace the whole thing with a multi-speed wet rotor. 10 CI Radiators. Money's tight so I'd rather not put in a modern B&G (HV or PR?). Anyone?

Posted Aug 29, 2018, 2:58 PM UTC · edited

15
zephyr2u•

Sorry. A new pump, impeller and housing is the only insurance. If you'fix' it, it all quit again.

2
sposdaOP•

Does the Honeywell PC3F4344IUF00 seem like a good replacement?

1
zephyr2u•

Frankly, I would choose the same Bell & Gossett pump because is connection, capacity, and quality.

1
sposdaOP•

But it's obsolete, so I don't have the performance curve to compare. I assume the HV pump was the replacement model, but is there a datasheet?

1
zephyr2u•

Yes you can check with bell and gossett they have a chart and diagram and can give you the replacement number

1