Small Surge Protector?

I work in the supermarket refrigeration industry.

I have a particular store that has 3 refrigeration racks that anytime there is a brownout or thunderstorm they loose multiple coils on the contractors.

Store is 208v. So is the control voltage on these contractors.

208v 3ph feeds the condenser. 2 phases feed the control circuit.

The contractors coils are RATED 208/230 but most of the time the voltage reads 200v.

So. I’m guessing the voltage drops during storms, etc and burns the coils up that are energized.

Phase monitors won’t work as the control board has a fail safe and all contractors pull in if the board loses power and this is fed off a 24v CT transformer off that same control voltage.

So, I’m thinking some kind of small voltage conditioner, surge protector, etc? Only pulls 2-3 amps. The fuse that blows is a FNQ 1 6/10.

Ideas?

Posted Sep 17, 2018, 7:12 PM UTC

110
a_tallguy[V] Red Seal Electrician•

I would certainly consider that to be a supply issue.

You really should be looking for an undervoltage relay that will stop the equipment from operating in those conditions and have a timer for when to resume operation.

I realize that refrigeration is important, but no surge protector is going to aid a brownout.

3
Topherlee75OP•

This is the closest thing to what I’ve had in mind.

The oddest thing is it only effects the condensers. None of the compressor contractors, fans for the evaporators, nothing but the condenser fan contactors. Not even anything in the AHU, which is also on the roof. And it’s not like the condenser power all comes from the same panels. One rack is on the other side of the store and it’s power comes from the sub panel in that motor room.

The UPS idea is ok. But implementing it would be difficult.

Low voltage relay, I thought about but then when the condenser shuts down the rack is still running and we run a high discharge pressure situation because the condenser fans are not running to reject the heat.

1
a_tallguy[V] Red Seal Electrician•

Is all the wiring sized appropriately for the load?

1
Topherlee75OP•

This location has been around 14 years. Every time there is a storm, we lose contactors. The same feed for each condenser also feeds the condenser motors, and a 24v CT transformer. The only this that happens is the coils burn up on the contactors. 2 or 3 times a years. Only happens during storms when the power has issues.

Each condenser has its own separate feed.

He control circuit in each condenser in question is protected by a FNQ 1 6/10 fuse. So less than 2 amps of current.

1
a_tallguy[V] Red Seal Electrician•

Is there an option to use a lower control voltage? It may be worth looking into.

1
Electron82•

A UPS not a surge protector if your having brownouts use a UPS

1
ithinarineJourneyman•

A UPS for a 208V 3-phase circuit that is potentially 20A or 30A? Are you kidding?

2

I mean they do make em for datacenters and whatnot. But wouldn’t be cheap

1
ithinarineJourneyman•

If you're only getting 200V under normal conditions, I would be calling the power company to come look at the transformer. 200V means you're only getting around 116V per phase, which is still within +/-5% of 120V, but it's definitely on the lower end of things, especially when on anywhere new, you would see closer to 124V per phase.

1