NEC Article 620 for residential attached garage installation (USA)
I'm looking for clarification on the requirements of NEC Article 620 on the installation of a safety switch for a vertical platform lift (VPL) in a residential attached garage.
*The VPL manufacturer calls for power supply installation compliant with NEC Article 620.
*My VPL installer ordered a GFCI with the safety switch.
*My Electrician said he didn't see anything on the spec sheet (which referenced Article 620) about the installation requiring a GFCI.
I did not get a GFCI on the electrical line with the safety switch. Does a safety switch need a GFCI or is it redundant? Does Article 620 call for a GFCI for a residential attached garage? I want to make sure this installation is safe and compliant as it is in my grandmother's house. Thank you in advance for any assistance.
Posted Jun 23, 2019, 7:21 PM UTC
GFCI protection for the lift circuit is only needed if the lift is getting power from a 15- or 20-amp 125-volt receptacle per NEC 210.8(A). The only requirements for GFCI protection in NEC 620 are for receptacles in specific locations related to the lift (620.85).
The receptacle is 120V 20A, so no GFCI is needed per NEC 210.8(A). Also, the receptacle is not within any of the locations specified in 620.85.
Thank you very much for clarifying!
Is that a typo? You would need GFCI protection if that's the case.
Woildnt garages be under 210.8(B), not A? A is for dwelling units, B is for not dwelling units.
garages are 210.8(a)(2)
not a typo, i'm confirming what trekkerscout said.
210.8(a) says 125v and my garage receptacle is not 125v (it is 120v), so i read that as it does not need gfci protection. if i'm not understanding the language, feel free to elaborate.
please be aware that i am not an electrician, i just have a copy of the NEC because anyone can buy a copy for $15. i am trying to understand why my electrician didn't install a gfci circuit when both the vpl mfg and the installer asked for one.
i will use the information provided here either to explain that a gfci is unnecessary to my vpl installers or justify calling the electrician out to fix their installation.
That's just a nominal value, it's a 120V receptacle. A receptacle in a garage needs GFCI protection by current code. But even regardless of code, if that's what the manufacturer's instructions called for then the electrician is obligated to follow those instructions.
If you guys are on the 2017 NEC this is the code section:
[deleted]