Educational resources for 3 phase
I need to learn three phase power and how solar works with it. It’s fairly confusing but I have to work past it. Any resources you can suggest. To get down to the exact question it is inverter selection and tie in. Do I need three inverters sized right. Can I just tie into 1 leg. Etc.
Posted Dec 14, 2019, 9:38 AM UTC
85
Depends on your local supply authority. We used to be able to use a single phase inverter on a three phase supply but now our network demands load is balanced over all three phases. So instead of using a single phase inverter and connecting to one leg you must use a three phase inverter. It makes more sense anyway as you are then supplying solar power to the entire installation and not just the circuits connected to one phase.
Ok. So I’m interested in theory at the moment. Anything that I can use to wrap my head around it all.
120/208 service I can use a solar edge 11.4 single phase which is 10@208 and I can do that just once. Not in multiples of 3.
Solar edge has a three phase 14.4. It can come with 2 more 14.4s. I could tie in just the 14.4. I don’t necessarily need all three (43.2 kW).
They also have a 9K. You can use any combination of the 9 and 14.4k because they output 3 phase.
If you use the single phase inverters, you could run into a problem with the utility straight up denying it. Even if you “phase balanced” the system they may not like it
Utilities are a drag. We have a main utility and 7 coops that all have their own rules. It’s a challenge.
I was looking at a 40kW cap and using 2 14.4s and a 9kw. That would be better than 4 11.4s treated as 10kWs at 208 voltage?
Would be much easier to approve