Educational resources for 3 phase

I need to learn three phase power and how solar works with it. It’s fairly confusing but I have to work past it. Any resources you can suggest. To get down to the exact question it is inverter selection and tie in. Do I need three inverters sized right. Can I just tie into 1 leg. Etc.

Posted Dec 14, 2019, 9:38 AM UTC

85
jmb-mtgsolar professional•

Depends on your local supply authority. We used to be able to use a single phase inverter on a three phase supply but now our network demands load is balanced over all three phases. So instead of using a single phase inverter and connecting to one leg you must use a three phase inverter. It makes more sense anyway as you are then supplying solar power to the entire installation and not just the circuits connected to one phase.

3
propanetableOP•

Ok. So I’m interested in theory at the moment. Anything that I can use to wrap my head around it all.

120/208 service I can use a solar edge 11.4 single phase which is 10@208 and I can do that just once. Not in multiples of 3.

Solar edge has a three phase 14.4. It can come with 2 more 14.4s. I could tie in just the 14.4. I don’t necessarily need all three (43.2 kW).

1
Garbluck•

They also have a 9K. You can use any combination of the 9 and 14.4k because they output 3 phase.

If you use the single phase inverters, you could run into a problem with the utility straight up denying it. Even if you “phase balanced” the system they may not like it

3
propanetableOP•

Utilities are a drag. We have a main utility and 7 coops that all have their own rules. It’s a challenge.

I was looking at a 40kW cap and using 2 14.4s and a 9kw. That would be better than 4 11.4s treated as 10kWs at 208 voltage?

1
Garbluck•

Would be much easier to approve

3
[deleted]•

[deleted]

1