Installed "ecobee Smart" 4 days ago, humidifier worked fine then stopped last night. With no call for humidity I see 12.5VAC between ACC+ and C?
EDIT: Solved as per the purpose of my post. I wanted to know if the 12.5VAC on the line was expected, and the rep ITT explained that it is expected. The ecobee sends out some sort of (sensing?) voltage when no equipment is connected, which I discovered in my testing and caused concern (12.5V constantly going to the relay/solenoid would be an issue) - but once the gear was reconnected as per his advice the voltage dropped to the expected 0.0V. The timing and odd voltage were cause for concern that the ecobee was involved in my humidifier failure, but it appears to all be coincidental and not related to the thermostat based on current information.
-------------------------Original:-------------------------
My humidifier stopped working last night. I bought the newest ecobee from my utility company a week ago and installed it on the 27th. Now, when I meter between the ecobee ACC+ and C, I get 12.5VAC?? Has the contact in the humidifier failed somehow to cause this? This should be 0V when there is no call for humidifier, correct?
After a full system power down and back up I am able to get 25VAC on that pair when there is a call for humidity, but when there is no call it drops to 12.5VAC instead of 0VAC. Any insight into what could be causing this?
Heat/Fan work fine. 28VAC between R and C at the board.
Posted Dec 31, 2019, 7:11 PM UTC · edited
What does it show for indoor humidity? There is a percentage of variance that the system will not call for the humidifier if the rh percentage is within the window that is normal. Taking showers, doing laundry, running the dishwasher all can affect indoor humidity levels. Unless your indoor humidity levels are in the low area 24/7 of below 45%, there really is no need to call for humidity.
I'm familiar with RH%. My house regularly drops below 20%RH without humidity reinforcement. I'm not asking why isn't it calling for it.
I'm forcing the unit to call for it or not based on the settings. I'm asking why it's giving partial voltage when I tell it not to call for humidifier. This is not expected behavior.