I found some single pole DC Breakers online. I'm going to use three strings in parallel to go to my charge controller. Can I tie all the negatives to one bus bar and then each of the three positives to three different Breakers on one side, and on the other side hook the three positives to a positive busbar going to the charge controller?

Posted Jan 27, 2020, 7:22 PM UTC

56
offthewallness•

That sounds like it would work to me. I set mine up a similar way.

3
FunlessOP•

Thank you.

2
Eschaton707•
2
FunlessOP•

Ah, so the combiner box is set up exactly like I'm talking about. Thank you.

1
Eschaton707•

Yep! Good luck and solar on!

1
ButchDeal•

It depends on your local code. You may have to use a breaker for the negative as well as the positive. The Breakers need to be rated for the voltage and for DC use and the combiner also needs to be rated.

More importantly if this is on a residential roof you may need to meet rapid shutdown (likely) as well as Arc fault interruption and/or ground fault interruption.

1