DIY Subpanel in Garage
Howdy!
First and foremost, I will be including a licensed electrician in all of this. I want to save on some cost, if possible, and do some of the electrical work myself in my own home (like running the wires). I want to run a subpanel to my garage. I'm having some trouble finding information on how the wire must be run through my attic.
The wire will need to run 75feet or so. I have 4 220v tools that I need to run in my garage but no more than 2 at a time (i.e. compressor and plasma). Do I need to drill holes in my joists and run wire through that or use conduit? Do you know of any resources that could help me get some information?
I've reached out to a few electricians to come out but with the recent coronvirus outbreak, most aren't meeting with customers. I will absolutely have an electrician do the hookups and configure the what I need. I just would like to save on some cost by running wires myself.
Posted Mar 22, 2020, 10:08 PM UTC
What is the size of your main service? What is the amperage of the tools you want to run in the garage? Is there open framing in the garage? What will you need to do to get from the main panel to the new sub panel location? Underground? Surface mounted conduit?
Honestly just hire someone. The number of times I’ve had a customer try to save a few bucks by doing the work themselves just meant I had more stuff to fix when I showed up. Like the best you can really do most of the time is clear all of your stuff out of the area I’m going to work in
This
I’ve got 150 amp service on my main. Wire will run through attic, completely inside. Each tool is under 30amps each so I could get away with a 60amp sub.
Go with 100 amp panel for more space. My sub panel is 200 amps, but limited by the breaker coming off the main panel and wire size.
Go with a 100 amp panel for all of the reasons above, but also because you've got some loads that will fluctuate greatly and may have high inrush current. That compressor will fit on whatever breaker it's sized for, but will draw significantly more power than the handle rating of the breaker at startup. It's only for a couple seconds so the breaker won't trip, but voltage drop can be an issue.
This would be #3 THHN for both phases and neutral (#2 if you upsize), and #6 for ground. 1" EMT would fit #3, barely for #2. 1 1/4" would pull a lot better, especially over that distance.
I second what the others are saying about hiring someone to do the entire thing. If I had a nickel for every time someone tried to save money this way I'd have a lot less money. Usually it ends up costing more, always in time. You can be off by 1" and now I've got to drill and punch out the top of the panel. You forgot the ground? Ok we'll empty the pipe and re-pull it. As others have said, making sure the workspace is clean and everything is accessible will help.