Adding GFI to NEMA 10-50R
Hi, asking for some advice. I am not an electrician (but do have an electronics engineering degree).
I have a workbench with some 110V equipment on it that is designed to plug into a NEMA 5-20R. Unfortunately, I don't have a 20A circuit there, and it's a rental so I don't want to make any changes. I do, however, have a NEMA 10-50R outlet. This can handle the current, and I believe I can wire to X and W or Y and W to get the 110V, but a 10-50R has no ground, and a lot of my equipment has the chassis connected to ground.
A lot of recommendations online say to wire ground to W (neutral), but I feel uneasy about this because then nothing would trip if current flowed to ground as that current would be indistinguishable from the current normally flowing on neutral right? I'm also not sure if a fault could cause the neutral on the 10-50R to become appreciably far from ground such that touching equipment enclosures could be dangerous.
What I was considering is to wire in a NEMA 5-20R GFCI outlet with ground wired to neutral. The outlet would be in an enclosure on the workbench, and I have a 10 AWG cable running from that to the 10-50R outlet. I also wanted to wire in a 20A breaker, but I don't really know how to do that in a handy box. If I can't do that safely, I will install a fuse in-line in the cable. I believe that would solve my concerns, but I would love if an actual certified electrician could let me know if that is a bad idea or not. Maybe none of this is even necessary and there is an easier option?
I'll give gold to the first person to give a comprehensive answer to the question. Thank you all for your time!
Posted Mar 29, 2020, 9:38 PM UTC
GFCIs will trip if the neutral/hot wires have a current imbalance. The ground pin on em' doesn't go through the thing that measures for the imbalance, it just gives a good spot for ground faults in the appliance to have a way to get home.
It'd be kinda useless if a GFCI didn't trip because the electrons found a way home through your body and into the floor, wouldn't it?
everything else seems fine to me - fireproof box, 20A fuse to protect the 20A outlet, good to go.
So you are saying that there probably is protection on the other end of the 50A circuit that doesn't need the ground pin? I.e if I were grounded and I were to touch the X or Y terminal on that outlet, something somewhere would trip? I wasn't aware of that, that is very useful information. Out of curiosity, how does that work when there is the X, Y and W pins. It's normal for I(X) != I(W) because some on the current may be going through Y for 220V appliances right?
No.. I wouldn't bet my life on there being a GFCI breaker on the other end inside the main panel. Keep that portable GFCI thing in your circuit.