Rotary UPS - any experiences good or bad?
I have just come across a data center with a rotary UPS today. What does r/sysadmin think about them compared to battery UPSes? Would this cause any red flags if you were looking for DC space for yourself?
Posted May 6, 2020, 9:16 PM UTC
They provide the magic number of "about 10 minutes" of power that you need because your ATS fails every time and you have to manually switch to the generator. The downside is that you cant really overbuild a flywheel like you can a UPS. For instance Eaton just swapped our batteries with new ones and now it will run for 90 minutes with the same load.
Really appreciate this perspective! This is about the number that was quoted, and they said due to this their generator design has to start up quicker. I am slightly wary because I have never of this before honestly!
Yeah well I have been responsible for all parts of a datacenter for about 22 years and when the utility fails having extra time to 'mess around with' the transfer switch before the batteries discharged fully has saved us at least 5 or 6 times. Transfer switches are the least reliable part of a DCs power infrastructure.
Flywheel gensets don't require transfer switches to activate, though, because they're in-line with the circuit and spinning constantly.
There is a transfer switch somewhere. between the a&b utility feeds.. etc.