I'm an electrician. I just installed a hard start kit and a new 55 5 capacitor in my ac yesterday. It worked as usual for about 24 hours. Now a fuse blew at the disconnect. I'm hoping it's just a coincidence.

Posted May 18, 2020, 11:49 PM UTC

29
Squirrelmasta23•

Check motor and compressor amp vs name plate rating if they check out prolly just weak fuse from cap not working properly

2
Smawesome•

Test your amps on start up and running

2
mist91OP•

I mention I'm an electrician because although I'm not an hvac guy, I know my way around electricity.

-1
ill-be_damned•

If your compressor needed the hard start she was on her way out. Sounds like burnt toast to me

2
mist91OP•

I don't know that it needed the hard start per se, it was something recommended so I just threw one on it. I figured it couldn't hurt.

-1
ColossusDrop•

Wrong. Hard starts are for emergencies. You have put unnecessary wear on your compressor

3
j3radley•

This is not correct.

Hard starts are a good idea on a compressor (even scroll) especially for heat pumps, TXV systems, older compressors that are struggling to start, and many other reasons.

The inrush period of a compressor start up can be five to seven times running amps. A hard start will shorten this time period by up to fifty percent.

1
ill-be_damned•

Bro if it’s not broke don’t fix it

1
bruh-brah•

You mean if it ain’t broke don’t brake it

1