I'm an electrician. I just installed a hard start kit and a new 55 5 capacitor in my ac yesterday. It worked as usual for about 24 hours. Now a fuse blew at the disconnect. I'm hoping it's just a coincidence.
Posted May 18, 2020, 11:49 PM UTC
Posted May 18, 2020, 11:49 PM UTC
Test your amps on start up and running
I mention I'm an electrician because although I'm not an hvac guy, I know my way around electricity.
If your compressor needed the hard start she was on her way out. Sounds like burnt toast to me
I don't know that it needed the hard start per se, it was something recommended so I just threw one on it. I figured it couldn't hurt.
Wrong. Hard starts are for emergencies. You have put unnecessary wear on your compressor
This is not correct.
Hard starts are a good idea on a compressor (even scroll) especially for heat pumps, TXV systems, older compressors that are struggling to start, and many other reasons.
The inrush period of a compressor start up can be five to seven times running amps. A hard start will shorten this time period by up to fifty percent.
Bro if it’s not broke don’t fix it
You mean if it ain’t broke don’t brake it
Check motor and compressor amp vs name plate rating if they check out prolly just weak fuse from cap not working properly