Improving a bonus room insulation.
I have a bonus room that needs to have the insulation situation improved. I have full access to the ceiling, one wall and two knee walls from the attic. Right now it’s just faced batting with the face toward the room. I have layed some unfaced r30 batting over some of the trouble areas as a temp solution.
The recommendation I keep getting is to essentially incase the whole thing in foam board and air seal it with expanding foam. From an insulation stand point that seems reasonable enough.
My concern is if I air seal it then both sides have a vapor barrier. Isn’t that a moisture problem? I am wondering if I should pull the faced insulation and put in unfaced. I can likely put a higher r value in at the same time.
Posted Jul 10, 2020, 9:40 PM UTC
That faced batting is NOT a vapor barrier. Never was, never will be. It is a convenient way to create a fiberglass batt, is all.
The foam board is a good recommendation, because it creates a thermal break between you and the attic heat.
I should have said vapor retardant.
So in general everything I see says to never lay faced batt on faced batt due to moister problems. Is there something I am missing with those recommendations?
The unsaid statement is that for it to be effective, it needs to be seamless. A hole the size of a quarter will let a gallon of water vapor through every year. When these are installed, no attempt is made to seal the edges. Water vapor is not inhibited in the slightest.