Autotransformers, inrush current, and portable generators.
Hi! I have an oddball question about transformer inrush, generators, and creating split-phase power from single-phase. I'll try my best to keep it as straightforward as possible, but buckle in regardless because I need to set the scene first.
The Problem
My family's house is powered by a 4KW 48vdc to split-phase 120+120=240vac inverter. The house is wired for a single phase of 120vac so only the inverter's L1 and N are connected. Originally the house was powered by a single-phase inverter. The inverter has an integrated battery charger and transfer switch to simultaneously pass through an external AC source while charging batteries. The inverter allows user-defined current limits to avoid overloading smaller generators. No electrical grid is present.
We're very lucky to have such an expensive and powerful inverter, however, it will only accept split-phase 120+120=240vac input for charging and passthrough. Occasionally the weather is very poor for an extended period of time. During those periods we'd like to charge our batteries off a generator. We possess only a 2.5KW single-phase 120vac inverter generator and a 2.3KW single-phase 120vac alternator generator. Two companies manufacture autotransformers capable of, among other things, accepting 120vac on one end and outputting 120+120=240vac on the other end. Purchasing or building a new split-phase generator costs as much as a car and we wish to avoid this option, using an existing generator, as an autotransformer is much less expensive and adds versatility.
The Actual Question
I am concerned about the inrush current the generators would experience when energizing the autotransformer. Before the initial magnetic field develops, the transformer will potentially draw an absurd amount of inrush current depending on when in the AC cycle the connection is made. I'm concerned that this could have a number of undesirable effects:
- Inverter in Inverter Generator too sensitive and trips out due to perceived short
- Breaker in Inverter Generator electromagnetically trips
- Breaker in Alternator Generator electromagnetically trips
How valid is this concern? Neither company states inrush current for their autotransformers in their manuals or datasheets. I lack the experience with transformers to make an educated guess at how well one of these units and a generator would get along. Obviously we can't really afford to lay out the money and time pursuing this solution blind if it could easily not work and leave us back where we started.
Thank you so much for taking the time to read my novel. Me and my family would really appreciate any insight into this. <3