ElectroBOOM installs IR patio heater.

Posted Dec 11, 2020, 6:17 PM UTC

157
g0tter[V] Journeyman•

Canadian Electrical Code violations

12-608 cable not mechanically secured to panel

12-610 (1)(a) - no anti-short bushing on armored cable

12-3034 - table 23 allows 4x #10 wires in that box, I count 8 (6 wire, 2 for the switch)

62-110 - that circuit should only be feeding the heater, not that receptacle as well

62-202 - i didn't see if the heater had an integral thermostat, if not it will need one

I'm sure i missed some too

13
bthpirnhf•

14-50R on #10 wire

5
fiestytreasure•

Well he still only has a 30A breaker so the cable is protected, but it will most likely trip if he uses 50A on the outlet. Not good, but I don't see a big problem with that point.

It only won't work as intended and lead to excessive tripping of the breaker and might lead to breaker failure though.

2
[deleted]•

[deleted]

1
dobsss•

Almost shat myself when he passed the BX through the panel.. LIVE

7
thenewmaricon20•

I am scared just watching him playing around the main breaker with everything live besides.

5
Eskoot195382•

Is ElectroBOOM liked or disliked here?

1
SnicksneeOP•

I’m a fan, but I’m EET, not an electrician. Don’t hate me.

1