How to find high density 0U PDUs?

Help

I must have spent a huge amount of time over the years looking at PDUs and feel like I'm missing something obvious somewhere.

How in the world am I supposed to power 48 power supplies for 24 servers in a 24u rack when all the PDUs have such low outlet counts? You can find a 24 outlet PDU that is 70 inches long.. where are the 24 outlet PDUs which are 42-46 inches long? There seems to be something horribly wrong with the availability of PDUs in density of 1 outlet per 1u of rack space. How does a company possibly have 42 1u dual-power servers in a single rack given the lack of available PDU solutions?

Posted Feb 26, 2021, 10:40 PM UTC

115
cjcox4•

Just get four 15 outlet zero U strips, double them up on each side.

3
TinyCollectionOP64 TB RAW•

What I really want is the 1U x 1 outlet setup so all the cords can be the same length even if I can only do 12u this way.

1
cjcox4•

1U with 24 outlets? No. Even with 2U, getting more than 20 would be difficult.

Hope you can find something that works. I still think just doubling up on the zero Us is your best bet.

2
TinyCollectionOP64 TB RAW•

You misunderstand my request. I desire a 0u vertical PDU which has all the outlets spaced exactly 1U apart. Even 12 total outlets would do wonders for cable management.

1
cjcox4•

Gotcha, but even full height cabinet PDU are usually not spaced 1U apart usually. I was merely trying to find something that would work that was vertical. I was hoping to find a double wide single unit. But didn't. So thought you might just bind two together.

2
gmc_5303•

I don’t think 24u racks are expected to have high server density counts because it’s 24u. Not the usual high density data center installation.

2
TinyCollectionOP64 TB RAW•

But a 42u rack is expected to have up to 42 servers and I can't find anything that density either. I just found an APC 15x C13 24" unit which might end up working tho its $199 each.

1
gmc_5303•

You have to start looking in the 400v, 60a 3 phase range like the ap8888 . 42 2 proc 1u servers can gobble a lot of power. That’s where the blade, multi server chassis, fat twins, and micro blades come into play.

3
TinyCollectionOP64 TB RAW•

It’s so weird how the bigger ones don’t have the outlets of the same types. They mix and match which must be hell on trying to cable that thing.

1
gmc_5303•

Also, racks can be setup to have 4 42u pdus in them. That’s still 84 power cables and it’s a lot to deal with. I have deep and wide racks and usually run two 42u pdus on one side and apc cable management fingers on the other. Works well given the variety of equipment (servers, storage, fc switches, tor switches, etc) that goes in my racks.

2
TinyCollectionOP64 TB RAW•

So you can buy 42u 42 outlet PDUs?

1
gmc_5303•

Yep. Lookup an ap8888 .

2
qupada42•

https://enlogic.com/legacy-products/EN1112

Here's a 48, but it's discontinued so you might have some trouble finding one.

Not quite the layout you wanted (has three banks, laid out with a+b, b+c and c+a phases so you've got resiliency without overly long cables), but meets the outlet count requirement.

1
TinyCollectionOP64 TB RAW•

That's basically PDU porn

2