240v Variable speed pool pump need a GFCI?

Hi everybody! I just installed a 240v variable speed hayward pool pump and wanted to update the electrical to current code. I found an electrician, got a quote to add gfci outlets and new switches plus install gfci protection to the pool pump.

Everyone is busy now and I get it, but they sent a green kid to run the conduit, so now it looks like I ran it myself. He also didn't put in GFCI protection for my pump. I called and they sent out the original electrician that gave me the quote and they're going to fix the conduit but he claims they never gfci protect pool pumps and that they don't have to. It's not against code. But everything I read says it is? He's arguing with me about doing it, and says it's not possible???

Does anyone have experience with pool pumps? I know older pools can be grandfathered in but I'd like the pump to be wired to current code as long as I'm updating. I also have 4 children I'd rather not electrocute.

Can somebody give me some ammo here? Did I hire a bad electrician or am I just a moron who doesn't understand the code???

Posted Apr 5, 2021, 6:39 PM UTC

327
iamjacksthirdeye•

NEC 680.21(C). All pool pumps require GFCI protection. If he still refuses to install a GFCI, call a 3rd party inspector to come out and fail his work. You might have hired a hack.

4
chompychompchompOP•

Thanks for the code. Appreciate it.

1
chompychompchompOP•

Hokay so I just got an email from the electrical company owner who said they only install gfci for the pool light and electrical boxes around the pool, not for the motor. I must have hired a hack :(

0
xveganxcowboyx•

While getting a code reference is great, it can be hard to tell who it applies to on worldwide forums like this. NEC is NOT a national standard. It's adopted directly by many states, but not at the same time. Some states modify it or write their own. Some states, like Arizona, do not adopt any code and leave it to local municipalities to decide what they would like to do.

You'll need to fine out what, if any, code your city or county operates under and what the permitting and enforcement mechanism is before anyone can say whether it's required.

1
chompychompchompOP•

I am actually in Arizona. I'm not worried about it being up to code so much as being as safe as it possibly can be. It seems like having the pump on a gfci circuit is the safest, but this electrician is refusing to do it for me because he says it's just not done.

I'm frustrated because I specifically asked for this and now he's acting like I'm crazy for even wanting it. If he had a good reason for not doing it I'd be fine with it, but he just keeps saying they just don't do it.

I do have a variable speed pump, so I don't actually know the rules for a variable speed pump. The code just mentions a single speed pump. I did read a crazy article arguing variable speed pumps don't need them because they'd be on a 25A circuit breaker but it reads like Greek to me.

I just wish the guy could explain why they don't do it (and why they won't, even if I'm willing to pay for it).

1
Flowchart83•

You have to GFCI protect anything regarding pools. What happens if there is a ground fault without one?!

3
chompychompchompOP•

Apparently we die!

0
Virtual-Reach•

Where are you located? In Canada there are specific circumstances that require gfci protection when referring to pools, but a remote pool pump is not one of them

3
chompychompchompOP•

In the United States. As I understand it the NEC rules changed in 2014 when it comes to pool pumps...but I might be totally wrong. I'm not an electrician... but I do want to do things right.

1
shaun_of_the_south•

I’m not saying this guys right or wrong but every place isn’t on the most current code.

2
Virtual-Reach•

So true, and every province /state has their own code addendums/edits

2

It's not even that - current codes don't apply to existing installations. You don't have to bring something "up to code" because you replaced a worn out pump. OP wants one anyway, which is different, but the electrical code isn't in play here.

1
NurseMan79•

Exterior and/or near water? Check and double check! Needs a gfci.

2
chrishiz•

So, he is probably saying that the 240v pool pump has no neutral and doesn’t need GFCI. Well I found out a couple years ago that even though there isn’t a neutral connected to breaker from load(GFCI breakers), it is still sensing leaky voltage to ground through that neutral jumper.

1
chompychompchompOP•

So it would still do the job, right? So should I push for it or just let it go?

1
chrishiz•

Push for it. All new installs would have GfCi protection to be code compliant.

1

He wants it, but it is a legacy installation. Purchasing a new pump doesn't trigger or require the electrics feeding the existing pool equipment be updated to the latest code. Just like a brand new range can be connected to a legacy 3-wire no ground range circuit.

0
chrishiz•

Well his second sentence says to include gfci pool pump protection.

1

The neutral being there or not has nothing to do with it. A straight 240 load on a 240 volt GFCI breaker senses an imbalance between L1 and L2, just like a 120 volt GFCI senses an imbalance between L and N.

1

You want it, and if they priced to put it in and didn't then there's a refund due unless they install one. By code you do not need it, your pool is existing before code required it for 240v pumps. The purchase of a new pump does not trigger or require the upgrading of the existing pool circuit electrics to meet the current or most recent code, even though when it comes to pools, the more safe the better. Depending on how your pump is fed, you may have a panel that is difficult to source GFCI breakers for, driving their hesitance to give you what you want. As an aside there had been a lot of posts about variable speed pumps tripping GFCIs so, fair warning.

Aside from the GFCI, the most critical part of pool wiring safety is that solid copper electrical bond wire you have on the outside.

1