Generator install

Hey everyone,

Finally getting around to wiring up our house for our portable generator. Should be pretty straightforward, new 240v 30amp breaker, 30 amp receptical, 10/3 wire with ground (Romex), pre-assembled 10/3 extension cord 25ft (nema 14-30), 1/2 ground rod , interlock, and some #8 for a ground wire.

Feel pretty good about the install but for those of you who have done this before was there something you wish you did differently or maybe a tip.

Thanks

Posted Jul 4, 2021, 12:35 AM UTC

327
l1thiumion•

Does this bond the neutral to ground when using the generator? I’ve always wondered that, since most gas furnaces want to see a bonded neutral to ground before it will ignite.

1
Way2ManyProjectsOP•

Yes, the neutral and ground will be bonded in my main house panel. The 30 amp inlet box that I’m mounting on my house will not have the neutral and ground bonded together.

2
nunuvyer•

The 30 amp inlet box that I’m mounting on my house will not have the neutral and ground bonded together.

No but your generator probably will, at a point inside the access panel at the end of the generator head. You should lift that bond.

1

What are you using for fuel?

1
Way2ManyProjectsOP•

At the moment super/premium gas with a stabilizer.

I ended up buying the propane conversion for it but I don’t think I’ll end up using it. If I already had propane I would be running it already

1

I paid $39.00 for the complete carburator assembly from eBay. No modifications.

If you are gonna run gas, get the ethynol free gas only. You are wasting your money on super/premium gas.

1
Way2ManyProjectsOP•

I got mine on Amazon back when I first bought the machine and I paid $40 or so for it. Haven’t used it but it looks decent.

Agreed, now that I’ll be using it more I’ll pick up an extra can. It didn’t make sense before because I wasn’t using it at all and I just used my dirt bike gas.

1
tsr6•

In my area the only ethanol free gas is premium gas.

1

Have you tried any marine fueling places?

Have you looked up ethynol free gas website? It lists stations by zip code?

1
KetoMan30•

Check out PNG Technologies out of Michigan. They offer natural gas conversion kits.

1
Way2ManyProjectsOP•

If I had a NG or propane tank in the yard or a way to get a line put in, that’s the first thing I would do. Since I don’t I’ll probably just stick with gas for now.

I could run it off 20 gallon propane tanks but I don’t think I want to right now

1
[deleted]•

[deleted]

1
Way2ManyProjectsOP•

Some generators need additional grounding. Check you manual and see. I know my predator “needs” additional grounding.

With that said, most people never ground the body of the generator and it’s fine. I’ve never seen anyone camping and they start hammering in a ground rod ha ha.

I’m just trying to cover everything because I’m going to have everything inspected after

1
nunuvyer•

If it's going to be inspected there needs to be an interlock between the generator breaker and the main breaker.

The neutral on the generator should NOT be bonded to ground. If it is, you need to separate them (lift the neutral jumper and tape it off). Once that is done, your house panel will supply the ground. You do not want TWO grounds in a system so do not connect the generator to a separate ground rod unless you are using it as a portable.

2
Way2ManyProjectsOP•

There will be an interlock on the main panel.

I’ll be wiring up the the 10/3 from my panel; two hots and the ground and neutral connected to the same bar in the panel

From there the 10/3 wire will be ran to the “reliance” 30 amp receptical.

From the generator I have a pre bought cord ( but it’s 10/3 wire nema 14-30)

Then a separate ground rod to bond the generator frame to ground.

If any of this is wrong please let me know. I’ve been going off the nema 2017 as that’s what my town uses.

1
nunuvyer•

Either you should ground the generator frame to a rod and then float the ground to the panel or else you should run the panel ground thru to your generator frame but not both.

2
[deleted]•

[deleted]

1
david5944•

I had my electrician install 8/3 instead of 10/3 for my 30 amp inlet. I figured it would future proof myself if I ever wanted to go to a 50 amp generator. We lost power last week and my voltage was a little lower than I expected and I had to think about how much wire gauge/length might be contributing. So if the pricing difference isnt much(which is a relative question) I'd consider a bigger cable for this segment.

1
Way2ManyProjectsOP•

I probably should have done that too but I wasn’t thinking that far ahead. 30 amps should be plenty for me unless something changes

How far is your run?

1
david5944•

Right around 50 feet from panel to inlet. So not short.

1