Hey everyone,
Finally getting around to wiring up our house for our portable generator. Should be pretty straightforward, new 240v 30amp breaker, 30 amp receptical, 10/3 wire with ground (Romex), pre-assembled 10/3 extension cord 25ft (nema 14-30), 1/2 ground rod , interlock, and some #8 for a ground wire.
Feel pretty good about the install but for those of you who have done this before was there something you wish you did differently or maybe a tip.
Thanks
Posted Jul 4, 2021, 12:35 AM UTC
Does this bond the neutral to ground when using the generator? I’ve always wondered that, since most gas furnaces want to see a bonded neutral to ground before it will ignite.
Yes, the neutral and ground will be bonded in my main house panel. The 30 amp inlet box that I’m mounting on my house will not have the neutral and ground bonded together.
The 30 amp inlet box that I’m mounting on my house will not have the neutral and ground bonded together.
No but your generator probably will, at a point inside the access panel at the end of the generator head. You should lift that bond.