Need suggestions troubleshooting 3amp low voltage fuse blowing.

Hi.. any help would be greatly appreciated... tried to turn on the ac the other day and nothing. Its an old Goodman. Turns out the 3 amp fuse on the low voltage side of the board was blown. So far i have disconnected all sensors and thermostat. Replaced the transformer and board. The fuse just keeps blowing. Ive traced all the lines on the Molex connector (that carries the 24vac to the board) and made sure all sensors are disconnected and there are no nicked wires. The control wire that goes out to the condenser is also disconnected. The board is free of the mounting chassis and not shorted to anything. Keeps on blowing on both the original board and the brand new one. Thanks.

Posted Jul 30, 2021, 3:55 AM UTC

115
ColossusDropApproved technician•

Did you have any electrical work done recently or do you have a homeless person underneath your house tapping power.

1
werd678OP•

No work done. But there is a person below. I dont think he's tapping power but that doesn't mean he's not. The transformer is putting out 28v (even though it's rated at 24v) I bought another one and it also put out 27v. I didn't think couple volts high would make much difference. I even tried putting a 4amp fuse in to compensate for that one time and even that blew.

1
ColossusDropApproved technician•

I suspect that something unusual, electrical wise, has changed. I'm not convinced that there's a short at the unit, not without being able to inspect it myself.

1
werd678OP•

Would it be on the HVAC circuit or could it be on another circuit. Would you recommend turning everything off but the HVAC circuit?

1
ColossusDropApproved technician•

I'm not an electrician so I'm not going to stick my neck out too far. It's possible that the wiring in your place has some shared connections with the guy downstairs and then that guy starts mixing and matching hots and neutrals from different circuits.

1
ALonelyWelcomeMatApproved Technician•

Its most likely wiring, you replaced the thermostat but it's still using the same wires. If you had a multimeter, I would unhook all the thermostat wires and check them against each other for continuity to see if they are touching each other inside the walls and causing a short.

If you don't have a meter, one thing you could do is unhook all the thermostat wires from the board, then one at a time hook them back in and turn it on. If you put a wire in and you turn it on, and the fuse pops, you know its that wire causing the short

1
werd678OP•

I did both of those. The fuse blows with the TS wires disconnected from the board. Also each wire has continuity from the wall to the other end at the unit. Also each of the wires is isolated from the others.

1
theelite1x87Approved technician•

So fuse blows even with NOTHING connected to the thermostat terminals on board? Yikes.... Well, something is drawing current. You may need a tech to come out and take a close look at board and wiring. The board could have malfunctioned internally on it's PCB causing a short circuit or their could be some sort of short circuit with other wiring from those molex connectors. You need a tech to come out and look over everything with a fine tooth comb before you condemn anything. Could be something as simple as a metal piece of debris stuck somewhere on PCB causing a short. I have not had this on HVAC equipment (yet) but I've had this issue with electronics before (retro game systems). Caused me hours of headaches until I saw the problem.

1
werd678OP•

Yea. Exactly what you described. Calling a tech tomorow but I was hoping someone on here would have some great trick I didn't think of. Whatever it is isn't on the board because like I said, I bought another board and it also blows fuses. So I'm thinking the molex.... Either metal/nick like you said (which I didn't see)

1
theelite1x87Approved technician•

Unfortunately no quick and dirty trick for this. Removing tstat wires to take Stat and wires out of equation is a good step. Beyond that you just need a good tech to poke around with meter and start ohming stuff out. Since you already swapped board and issue remains then it's clearly a problem with existing wiring inside unit but to find out what and how to fix it requires patience and a meter.

1
Hardscapes1400•

How old is the system and thermostat wiring? Sounds like a low voltage short, most likely in the thermostat wiring or miswired, did you replace the stat? 27-28v out of the transformer will not blow the fuse, if you pull all the wire from the thermostat ONLY does the fuse blow? (R,G,Y,C,W)

1
werd678OP•

It's old. 15+ yrs. But the wires don't look bad. Also did continuity and isolation test on them. Didn't replace the stat but took those wires off the board. I think I did remove tstat wiress only and it blew... I think that was one of the first things I did.

1