How to check charge on a heat pump with a piston during winter?

Heat Pump

Title says it all, I'm trying to figure out how to check our heat pumps during winter and I'm getting confused. Some say consult the pressure temp chart on the unit but most of our units don't have that, others say wrap the outdoor in a blanket and put it in A/c and check super heat but we didnt have something applicable for a blanket so I used a big trash bag and idk how accurate that'd be meanwhile some just say get the line temp to 100°f above outdoor ambient. What would the proper way be to check the charge on these systems? We have R22 and 410a any help would be greatly appreciated

Posted Dec 23, 2021, 9:13 PM UTC

06
se160•

What problems are you experiencing with the system? Shouldn’t be putting gauges on it if everything’s working fine

1
NitroMetaOP•

No heat calls output is 73°f with outdoor temp around 40-50°f

1
se160•

Are you sure the compressor is running? What is your head pressure? How is indoor airflow?

1
NitroMetaOP•

Compressor is running pipe is warm, air flow is good i don't remember the head pressure but the true suction was about 70ish psi R22. We've had a bunch of techs who didn't charge units with superheat and I believe this is one of those mischarged units

1
Badprimerib•

All you can do is get somewhat close by using the charts that come with the outdoor unit. However lineset length/rise, indoor airflow, and especially which indoor coil you use can all swing it a LOT.

1
TechnicalLeeApproved technician•

Using an app like MeasureQuick with all the probes is the best way. If you are a pro, it's worth the investment. If you don't have the equipment for that, then you'll have to rely on pressure/temp charts and or subcool/superheat methods. You might have to look up the P/T chart with the model number online, or call tech support.

https://www.youtube.com/watch?v=VLwW67jA4lw

https://hvacrschool.com/refrigerant-charging-basics-for-air-conditioning-heat-pump-systems/

1