conair_93Approved technician•

You need to replace the leaking component before firing the boiler. It’s not a good idea to run your boiler without a make-up water.

2
pj91198Approved technician•

Yeah you should have the waterfeed replaced. If its super cold out and the boiler is 10-20psi then you should be able to fire it with the valves closed but Id check the pressure morning/afternoon and evening until its replaced.

2
GrownTommyApproved Technician•

Are you able to close the bleeder shut? If not you need a new bleed valve. Shutting those valves off won’t circulate water and won’t be heating anything.

0