Dodgy rangehood wiring - Suggestions?

Posted Jan 29, 2022, 1:13 AM UTC

Posted Jan 29, 2022, 1:13 AM UTC
All the wires look concealed?
Yeah, I was more thinking of the terminal block on the outlet - the screw-downs are bare, and presumably live, and the shroud has a bunch of holes things could be poked in.
Just discovered this while I was prepping to paint - Lots of ever-so-slightly dodgy work around the place I've been trying to fix up as I go, but this is the first electrical one that's made me shudder. This plug was floating free in the ducting cover, and basically fell out when I got it off.
Anyone got any reckons on how to tidy this up, and not have these wire terminals sitting exposed inside a piece of stainless?
Either a mount block on the wall or drill through top plate of wall put cable in wall and put a flush box in the wall and fit the outlet like it should have been done.
https://www.kiwisparks.co.nz/products/pdl-deep-mounting-block
This could work. Could also put it in the ceiling as the other commenter mentioned (if you have access)
Was about to suggest this. Cheapest way to make it safe.
Seems legit
Poke the lot back up into the ceiling, and forget about it. That's what I'd do.
Yeah, nah. The hole is way too small to get the whole outlet arrangement up into the ceiling.
But also, I like my house not suffering from electrical fires
Each to their own.
Just take the socket off and replace it with a female plug. You don't need a switch there you can't access it anyway, it will have a switch somewhere else
Happy to be corrected, but I think you have to have a switch legally.
Also you shouldn't wire TPS into a female plug. Plugs are made for flexible cable.
While that correct it will still be considerably safer that what OP has now and as its not going to be unplugged regularly it wont cause any issue, he has next to no room to mount what he has
Yup, it's meant to be able to be switched from where it's operated. Been pulled up on a similar situation to op.
That's not correct, the isolator will be the MCB at the switchboard, any functional switch in the kitchen will be purely for convenience, or inconvenience where fridges are concerned
It does have to be switched, but I'd like to see you get to that switch to turn it off when the cover is back on, the entire point of an isolator is to isolate the appliance with out having to touch it
Which it why I pointed out that it will be switched somewhere else
Distance from appliance is an issue as well. Had this problem with a louvre install that needed a second switch installed to comply.
There are still people putting range isolators behind the range/cooktop
The circuit breaker at the switchboard is the only switch needed
the circuit breaker is not a switch, you have no clue what you are talking about, any appliance must be able to be isolated with a switch within 2m, once that cover goes back on its not accessible so is required to have another switch
I assume the black cord is the power for the rangehood and the white TPS is the supply.
This is typically mounted inside the roof however that socket is wrong for the application. I would pull the cables inside the roof and replace the socket with something similar to this https://www.pdl.co.nz/products/detail?CatNo=413&itemno=413-WE&tab-document-1=0
Oh yeah, that sounds like a good solution, one of those should fit in the ceiling much more nicely