BluOn replacement Freon? What do I need to know?
Posted Jun 29, 2022, 10:46 PM UTC
Posted Jun 29, 2022, 10:46 PM UTC
You can't get 407c or 422b?
Not a darn drop either. BluOn that’s it. And only 2 cans of it. It going to get ugly here
Bluon is an overpriced imitation of R-422B or R-438A. Bluon also has limited distribution. Look for NU-22B branded R-422B. Made in Louisville, not China.
No R22 anywhere. What do I need to know about BluOn? It’s all I can buy. Any tips?
Says drop in replacement for r22 evacuate vacuum recharge
No oil change or adding poe oil?
Their website says no, also lower pressure.
Adjusting metering devices?
Not sure, didn't look into it that far but it said direct replacement. I rarely use 22 or replacements for it, most of my work was new construction/tenant fit outs and now vrf service which is pink can juice.
Where the fk are you in Canada that you can't buy anything but Bluon?
Saskatchewan apparently. And only 2 cans of BluOn. I am told there is more coming next week.
I havent had to use it yet, but I just used 100 lbs of r-22 and had a conversation with the parts house guy about bluon. Apparently on larger systems some will need txvs adjusted but you can lookup the model # of most units on the bluon app and it will tell you. I have used their tech support once and seems pretty legit. You're paying for a product not just refrigerant. That product (bluon) has pretty good support.
I just walked away from mine for the weekend. I have 2 stuck txv’s and added the renew before start up. I can’t adjust my txv’s. Suction 0. O superheat and just white washing the compressors instantly. I can’t get my txv’s to do anything when I try to set them. I am just not able to get my head around 0 suction and a suction line flooded with liquid. It defies logic. I check the fan, rotation, coil cleanliness and bulbs 100 times. This didn’t go so well. The head is around 185. I didn’t bother with sub cooling as I have bigger issues. It didn’t like BluOn
Download the Bluon pro app, free to register and such. You can type in the model number and serial number for the unit and the app will suggest potentially adjusting the TXV and provide instructions.
You might also want to switch the low pressure switch as Bluon runs a bit lower pressure. They also suggest installing a new filter dryer. Lastly charge to 80% of factory charge then finish off charging to get desired pressures. I have converted quiet a few old r22 package units and wall shakers with no issues so far. Hope it helps. Sorry for format typing on mobile.
Perfect reply. So just like any other conversion than! I am also adding a shot of that oil for sticky txv’s to each compressor as the unit was open to the air for a bit. Someone actually stole the R 22 out of this unit. Professionally stolen.
I always add ac renew when I switch them over, most of my units are 15 years old so anything to help them limp along. Good luck!
Does that renew free up txv’s too? These txv’s have been sticky on start up in the past. And how do add that stuff? Can I just suck it in the discharge under a vacuum?
Yes, copeland compressors changed the oil inside most of there compressors around 10 yrs ago to save cost. Studies (techs) found the oil wasn’t able to handle the compression and temperatures, so it gunked up and created a paste like substance. That substance clogged the driers and txvs.copelands fix/memo was to inject each circuit/system with ac renew . I was lucky enough to find this out only after changing 3 txv’s on a york package unit
Yes AC renew works great. It's the only additive I ever use
How much cold juice was in there to make that worth it?
6.3lbs a side. 12.6 total. They took my new filters too. The ass will probably come back for the copper tonight.
Seems like a lot of work for maybe $500 in refrigerant. That blows.