r/newzealand•
Transidental

Excessive electricity usage. Anyone know if you can use your smart meter to see your current house power draw?

Advice

I've found our house is drawing way too much eletricity, like over 100 kWh a day.
I'm wanting to use a process of elimination to isolate the most offending device or if something is outright not right with the meter (because this usage is insanely too high) or how my power company is getting the data.

On my smart meter I see a couple of settings that may be telling me what what current draw is but not sure which is correct for current draw (if any).

First one says a "PH" on the left of the screen and then a number that is currently 9.4 (ish) but now kW or anything else on the screen other than a flashing R in a circle. I thought PH could mean per hour but the strange thing with this number is it goes up with less devices on and down with more devices on - doesn't seem related to power draw.

The second is has what looks like a small t on the left and then a capital P and then a number that is currently 2.5 and a flash kW above the number (also the flashing R in a circle).

The second number I can get to change by turning things off and on so I am guessing that might be the draw but is that in hours or half hours?

The power company data they send me is measured in half hour lots. If I take the worst reading I can see between 6PM and 7PM on one day it reads:
6:00 - 6:30pm = 4.556 6:30 - 7:00 pm = 3.6

That's a whopping 8.1 KwH usage for that hour. No matter how many device I turn on though I can never get that second number I mention above in the power meter to anywhere near this.

I can get it to about 4.5 with the flashing kW which made me think maybe it's per half hour and not hour?

Does this power draw seem incredibly excessive either way? Using 2 x heat pumps set at a moderate temperature of around 18-20 (set it lower over night). One is a 7Kw unit though (other is 2Kw I believe) but again, doesn't appear to run all that often and surely wouldn't be fully drawing that much all the time?
Otherwise just standard devices of a PC running, usual hot water usage for a 4 person household etc.

It's basically DOUBLE what our previous house was and we were running ducted heat pump 24/7, spa pool and otherwise similar water usage and device usage to where we are now. I expected things to go down, not double.

Failing figuring this out myself is there anyone you can get in to investigate all this who can definitively find out what is drawing so much power or perhaps if something is wrong with the meter? It almost seems like it's sending through double the data it should i.e. sending a KwH rating every half hour instead of per hour?

Anyone ever encounter anything like this before and find a solution? Does it seem like this level of power draw is logical considering the above mentioned?

Posted Jul 27, 2022, 11:48 PM UTC

1243
Monkiknow•

had a massive spike in power usage a few months ago, turns out the hot water cylinder was blasting hot water out the roof and constantly refilling/ reheating 24/7.

12
TransidentalOP•

Thought that could be the case but our hot water was only heating 11pm to 7am so wouldn't explain the massive spikes like what I mentioned previously at 6pm to 7pm

2
EuphoricMilk•

Could also be set too high meaning it's evaporating in the tank and refilling.

3
unbenned•

Evaporating in the tank? Like boiling?

1
Hubris2•

Do most cylinders give you the ability to set charging to occur during certain hours? I had a new one installed last year but the plumber didn't ask anything about hours of charging, and it certainly doesn't have a screen or the kind of user interface I'd expect if this were intended for easy control. I guess I need to get a model# and search online.

1
TransidentalOP•

No idea, we needed to get a sparky out to change it.

1
LimeRum•

Check if your housemates got a grow wardrobe 😉

11
EuphoricMilk•

LOAD is what you're looking for. Shows the current load on your house

10
EuphoricMilk•

Turn everything off. Check the load screen. Note that figure down. Then turn on an individual appliances or item you want to test. Subtract the two figures to get a rough idea of how much that thing is consuming.

16
TransidentalOP•

Can't find a setting that shows LOAD, my old house had one and it said exactly that.

On the main screen it has a meter read for night and day seperately and then a time and date. That's the 4 options I can see by just pushing the button.

If I hold the button down for a few second I end up on a second screen of data which I refer in my post (PH and t P) with the t P seeming to change as I change what devices are running (e.g. I just turned both heat pumps off and it went from 2.8 down to 0.5).

I am GUESSING this is the load screen without it saying load but I was hoping someone maybe knew what the t P meant to confirm.

Also the second strange part is no matter how many devices I turn on - I can get it nowhere near a 8 KwH load like what my power company has recorded (and they are regularly getting 6+). The highest I've managed to get it is around 5 when both heat pumps are fully cranked and hot water is heating etc.

It's almost like this figure is per half hour but even then ... 8 KwH for those devices is insanely too high.

Could something be going wrong that somehow my data is doubling up in what is sent to the power company?

5
ComeAlongPonds•

LOAD was moved to Set B with recent firmware setting & renamed ANPS (amps) & t p (Active Power in kWh). Push & hold Select until Set A changes to set B, then press Select to cycle to see the options. From you pic you've found it.

2
untimely-end•

Google the meter makers name and model number, you’ll most likely find an operators manual for it which should tell you how to identify and manually extract specific readings (if your meter doesn’t automatically cycle through them). However I should also say that on our particular meter that function appears to have been disabled and it lately only shows the display test, 24 hour reading and date/time. Last time I looked (pre 2020?) it was possible to get signal strength, instantaneous load etc

E: meter is EDMI Atlas Mk7c

6
southstormy•

Failing figuring this out myself is there anyone you can get in to investigate all this who can definitively find out what is drawing so much power or perhaps if something is wrong with the meter?

Will cost obviously, but an electrician should be able to get to the bottom of it. Even if it's an intermittent issue I think they'd be able to install some temporary loggers on the switchboard, eg for 48 hours.

4
TransidentalOP•

I'll flick the property manager an email to get someone out to take a look. Don't think I should generally need pay for this myself.

3
awherewas•

hot water system. turn it off and take a reading. turn it on and read again over the same period. It is the most likely thing that breaks and does this. The heater element goes rogue and burns juice without heating your water the way it should. Fixing it is a landlord's problem

3
TransidentalOP•

Out of curiosity what should I expect for the hot water system?

For example I saw a spike in load just before, switched it off and it dropped meaning it was drawing about 4-5 KW, what I don't know is how long it may have continued to do this for.

I noted also just now it was cranked up to 70 inside the panel so I've turned this down to just over 60 which seems to be the recommendation which might help.

Is the best way to test it to try and leave it off for 24 hours to see how much a 24 hour draw changes by?

1
Default_WLG•

Hot water heating elements typically draw 2kW or 3kW. If it was running constantly (say, because you've got a hot water leak or faulty thermostat), it would use around 48kWh per day (2kW element) or 72kWh per day (3kW element). The hot water element power rating should be written on the tank somewhere - it might say 2000W or 3000W rather than 2kW/3kW though

3
Frosty-Grab•

My friend had a similar issue. The thermostat was gone in the hot water cylinder. It was boiling the water which was coming out an overflow and just kept going.

2
tagumi•

We're having the exact same thing going on at ours in a new place. Are you with octopus energy perchance? Can't get out t P reading to ever reach as high as our hourly billing suggests.

1
awherewas•

sorry i take so long. the thing is going to be on 24/7. it never turns off because the thermostat is not controlling it.

1
mattyandco•

Hot water leak somewhere? If the cylinder is electric.

3
TransidentalOP•

I'd thought so but the clincher on that is the hot water only turned on heating at about 11pm (landlord had it set there) so wouldn't explain the crazy usage at other times of the day.

Also I can not get the meter to show a load (assuming the number I'm looking at is kWh and now kW per half hour for some odd reason) anywhere near what I'm being told I'm consuming by the power company so something doesn't seem right.,

2
mattyandco•

It might be worth posting a picture of your meter for others to point things out on. If you do so just be sure to cover the identifier for that meter.

1
TransidentalOP•

https://imgur.com/a/k1sUcy9 is the setting and current "i assume" draw it shows.

As mentioned thatn umber changes as I turn off and on devices and look about what I would expect the KwH to be, but power company almost seem to treat it as a half hourly figure.

1
mattyandco•

https://www.camax.co.uk/downloads/EDMI-Atlas-Hardware-Reference-Manual-Revision-M.pdf

Well that's the manual for that meter (and like 3 other variations) mostly install instructions but it does go over the display.

2
Revolutionaryear17•

Is that a 'hard' restriction. It might have a temperature probe to make sure the water doesn't go below safe temperatures.

What is your water bill like?

1
TransidentalOP•

It was a hard restriction yes, we are looking to get a sparky to change it back to anytime but waiting to solve this power usage issue first.

1
Last_Vanguard•

Do you live with anyone else? Maybe someone has discovered crypto mining and running their GPU at full tilt.

3
TransidentalOP•

My issue is more I can't get my meter draw at any point in time to align with the hourly usage stats coming from my power company.

e.g. if power company shows that in some hours I use 8 KwH then by turning everything possibly on that I would use and ensuring hot water is heating then I should see a simil;ar number for current usage on my meter.

1
Ok-Discount-2818•

We have a crypto miner in our basement 🤣🤣🤣 and it's power use isnt that bad. One shower uses more power in hot water than the PC uses in a day.

-4
7FOOT7•

This is bad. First step is to talk to your landlord, and the distribution company and if you have one a friendly electrician. This is a potentially dangerous technical problem that needs professional help. And now you know there is a problem you need to minimise harm.

https://comcom.govt.nz/regulated-industries/electricity-lines/electricity-distributor-map

A house on average uses about 7,000 kWh of electricity, but the amount used depends where in New Zealand you're living and how your house and hot water are heated. In 2017 average residential consumption varied from about 5,870 kWh on the West Coast to 8,550 kWh in Canterbury.

I make that about 20 kWh a day. A 2000W hot water heater would use 48kWh a day if left running non stop.

3
TransidentalOP•

And here I am using over 100 ... yeah something doesn't seem right

1
fraustnaut•

You can check which circuit is pulling all the load using your main switch board while checking your meter load.

1
TransidentalOP•

The problem is the load on my meter or "total active power kW" as its called in the manual looks to be about right. Right now it's 2.5 with both heat pumps running and that seems normal to me.

The problem though is I don't know if that's total active power per kwH or kW half hour.

It almost seems like it's per hour but I'm being billed per half hour? The usage data that the power company send me is per half hour and that seems to match the 'total active power' from my meter.

It's almost like something has gone wrong and I'm being billed my hourly usage every half hour instead?

1
Default_WLG•

It's 'per hour'. E.g. 1kW constant draw = 1kWh (kW-hours) consumed each hour. E.g. 3kW constant draw = 1.5kWh in half an hour. The meter should display totals over all time (in kWh) and instantaneous draw 'right now' (in kW). I believe it sends the totals back to the power company every half hour, and that's how they know your half-hourly usage.

2
tagumi•

Did you ever resolve this? By my estimates our usage is about 2x more than expected.

1
AntiSquidBurpMum•

When you find out what was doing it, please let us know!

I assume you've checked loft and/or basement or shed for landlord's cannabis plantation?

2
NZ_Si•

Hold the select button down for a second on the meter and it changes the measurements it cycles through each subsequent press. Switch it to current and start flicking breakers to isolate the circuit then move on to individual sockets assuming it isn't something on it's own breaker.

2
TransidentalOP•

The only time I've managed to see the current load get anywhere near the 7-10 kwh that powershop load has shown in many hour gaps is when water is heating.

However our water was SUPPOSED to only be heating between 11pm and 7am and this made sense because with a few showers in the morning you'd be out of hot water after 1 or 2 in the evening meaning nothing had heated.

However the big power draw was still showing in those times as though it was heating without heating.

1
no-pun-in-ten-did•

I have dealt with this. Our smart meter was putting out insane numbers. We calculated that it was reading more way power usage than we could actually draw - up to 28 kwh in one half hour. Contact was ridiculously unhelpful in sorting this out, and after fighting them for months over $800+ bills they took the unit back and accidentally destroyed it instead of auditing it like we asked. The bills were only refunded when we had escalated to the step of complaining to the ombudsman. The lower level support staff wouldn't look at the numbers and see that there was something wrong with an entire month's worth of energy being used in one day.

2
[deleted]•

[deleted]

1
10yearsnoaccount•

100KWh?!

that is almost certainly going to be the hot water cylinder

1
piroskamcs•

HWC. They turn on and off, and the power cos also turn them off, you'll get a spike when it comes back on as it heats back to the set temp.

And of course as hot water gets used, cold needs to be heated, plus the maintaining it at that temp.

1
TransidentalOP•

Indeed but not enough to warrant that sort of cost.

It's double my previous property and that too had a similarly sized and rated hwc with similar usage.

1
piroskamcs•

Maybe it's leaking? Go look under house, or if it has a tray in there. And if low pressure, the roof overflow.

1