P Trap doesn’t appear to drain unless I open vertical cap
Hello!
I have a weird situation where my P trap doesn’t appear to be doing any draining, however, if I open the vertical cap on it I see water start streaming (not heavily) in and it drains down the condensate line. Additionally, I feel cold air blow up through the vertical opening, is this all normal? It seems like it should be draining with the cap closed, but I don’t know enough about negative pressure and whatnot to understand it.
One other note, if I cover the open top with my hand I feel like a gurgling sensation until I remove my hand where it starts to drain again
Thanks!
Posted Sep 21, 2022, 4:49 AM UTC · edited
212
If it is a long run then it needs the venting
So cap off? What about the air blowing out when it’s open? Sorry, I’m a novice at this stuff, I appreciate your help though!
U can install a trap and install the vent after the trap
The weird thing is there is a vent after the trap (I attached a screenshot on this post) but it doesn’t seem to be enough? Not sure
Make sure its sloped properly 1 in for every 6 ft
https://prnt.sc/3C22jF3hstNh
Here is what it looks like if it helps
That is a trap it should flow with the red cap on
Make sure slope of drain is 1 in for every 6 ft
Or u can install a condensate pump that's what I usually do if drain is 30ft away it cost the same as 3 lengths of cpvc + fittings +labor