Honeywell T5. Heat not shutting off when hitting set temperature. Was not an issue this summer with cooling. Advice?

Just as the title says. Installed a T5 in June and everything ran as should with the A/C. Went to run the heat to make sure everything was good before it got cold and turned the unit to heat to 68. Furnace fired up and ran as should but never shut off once it hit the set point. I switched the unit off and it continued to run for 10 minutes while the temp continued to climb. I finally turned the unit to cool for 30 seconds and then to off and everything shut down. I have a heat pump set up with Electric back up. Any thoughts?

Posted Oct 20, 2022, 1:36 AM UTC

13
atypicallemon•

Look in the manual. The heat pump with the Honeywell stat says you cannot use w1 with a heat pump. It must be on w2. Look through the install manual though to verify. Usually when the ac goes off the furnace starts running.

2

Hows your t5 wiring look?

2
JohnnyDeereOP•

The guy that installed it had to use a C wire adapter. Behind the base I have the following Blue to C Pink to W White to K Red to R

1