Blowing a load in the hot tub

NSFW

I have an old spa that I want to put on a timer so that it's not noisy at night. The problem is that it's on a 15a plug, therefore typical 10a plug-n-play timers won't work. The second issue is that it has an RCD, which means any timer before the RCD in the circuit will trigger the RCD (meaning it wouldn't come back on again until that is reset). Is there a way of installing a timer after the RCD somehow? I apologise for the filthy title...

Posted Jul 9, 2023, 8:46 PM UTC

2427

You are not sorry, not at all :-)

25
yugiyo•

Shelly 3EM on the board would allow you to control a contactor (also on the board), and to monitor power use.

8
catchthelightOP•

Unfortunately that would trip the RCD :(

1
yugiyo•

Ah yeah, sorry thought the RCD was on the board.

2
catchthelightOP•

No worries, it feels so needlessly complicated. I'm now thinking of putting in an RCD/MCB combo on the board, and a wifi-relay behind the socket (Shelly 1PM) to control the timing.

1
yugiyo•

Yeah some wouldn't feel comfortable with the Shelly 1PM on a reasonably continuous 15A, though they are rated for it (and my hot water cylinder hasn't blown one up over the past year).

1
nzsp•

this is my exact setup

1
fuckingreddit666•

Just get a timer installed in the switchboard, I would put it before the RCD if it's a switchboard mounted RCD so if the RCD operates the timer won't need to be reset. Turning the power off to a switchboard mounted RCD shouldn't cause it to operate

3
catchthelightOP•

The RCD I currently have is on the spa lead unfortunately and so it does trip when the power is interrupted. It would be easy to remove, but I'm not sure how tricky/expensive it would be to put everything on the switchboard. Maybe I'll chat to a sparky to get a ballpark figure. I was hoping there would be a way to retrofit one inline nearer the spa end of the circuit, but accept it may not be possible.

2
Chrispy101010•

You could put a timer inside the spa, after the RCD instead. It would need IP rated. PDL used to do a weatherproof one in 56 series but it seems to have been discontinued. Ideally you'd want one with battery backup. Otherwise every time the RCD tripped the time would be wrong.

2
catchthelightOP•

Thank you, I'm leaning towards that idea. PDL56TC24HBLEGY looks perfect but it's a shame it's discontinued. I'll keep searching...

1
[deleted]•

[removed]

1
loose_as_a_moose•

You want to search for a 'time switch' or similar. They're used a lot in indistrual settings and HVAC. They're DIN mountable so you can feed it after the RCD or mount it in its own panel in the spa.

3
loose_as_a_moose•

Just had a thought, you can possibly get one with an RCD integrated. They also have bluetooth or zigbee integration these days.

Benefit of the "smart" version is that you can update it remotely, switch it and get power reporting which would be good for a spa. Especially for things like low power rates.

1
catchthelightOP•

Thanks - I am leaning towards that idea of mounting a timer on a panel next to the motor in the spa. The only problem is finding a 16amp IP-rated timer, as I can't find any let alone with smart/RCD integration.

1
loose_as_a_moose•

I couldn't tell you the exact code compliance but I think you can install a weatherproof panel in the spa and put the equipment in that. Timer/relay and current sensing included. It'll certainly be safe, still RCD protected, just unsure if it would meet regulatory scrutiny.

Getting to be a pretty involved project though. Surely a DIN mounted timer in the homes panel is more effective at that point.

3
falcon5nzSparky•

You can always use a contactor/relay.

1
TechE2020•

Yep, often the sparkies refer to them as "time clocks".

1
TechE2020•

I'm only aware of the plug-in RCDs that automatically trip if the power is off. I think that is a safety feature for power tools since panel-mounted RCDs do not trip when power is lost.

Consider using an RCD powerpoint or an RCD for the circuit in the switchboard. Then you can use any timer you want.

The Shelly Plus 1PM handles up to 16A, but the size of the screw terminals is a bit marginal for 16A continuous IMHO. I had one controlling a HWC for 2 years without trouble, but would personally go for an MCB-style timer (often called a time clock). There are some nice smart breakers that look great available from overseas, but they do not have an SDoC, so a bit of a moot point.

3
thecraftsman21•

Does the 15a socket have a dedicated feed? I.e. if you turn off the circuit breaker that feeds the spa socket, does anything else go dead too? If it's a dedicated feed then I would get an electrician to install an RCD and timer at the switchboard. Cleanest solution. Shelly devices are great if you like to control everything off your phone but if you just want a timer that does the same thing every day of the year and never think about it again then you don't have the hassle of faffing about with setting it all up on a device. However if you would like to have control over it yourself (and don't want to dick around with a timer on a switchboard) then a shelly device would be the way to go.

2
catchthelightOP•

Thank you, that's probably good advice as it is on its own dedicated circuit. The switchboard is quite old so admittedly I was worried about the messiness of adding an RCD and timer onto the board alongside the CB, but I guess the sparky will be able to tell me pretty quickly what is possible and what isn't. And if it isn't then a shelly can be the backup plan.

1
Tabdelineated•

Something like this? Probably need to get an electrician to install it

1
Novel_Agency_8443•

You can get 15a timers, I think a spa shop will have these. The rcd element I'm not sure, perhaps somtype of electronic controller?

1
WanGH2•

Errrr….

1