r/Nest•
Pewpasaurus

Damper on *. Equipment type setting? [Thermostat]

Thermostat

After a long bit of troubleshooting with Nest support, I set up my 2 zone home with two thermostats and wired the dampers into the * slot. I think this is working (one of my dampers has been broken since before the install, though), but the thermostats ask me what equipment is wired into * and dampers isn't an option. What should I put as that or am I wired up wrong?

Edit: Wiring/settings

Posted Jan 12, 2020, 8:23 PM UTC · edited

25
DrkMithNorCal Nest Pro•

The dampers are suposed to be controlled by the HZ221 zone damper controller not the nest........what is wired into the "Damper" terminals of the zone controller?

The nest should be connected to the HZ221 zone controller with "Rc"(or Rh), C, (O)O/B, G, Y1, Aux

The dampers should be connected to the zone damper terminals on the HZ221 controller

2
PewpasaurusOP•

Thanks, I meant that the AUX on the AZ221 is currently plugged into the *. Now that I think about it, when I was trying to troubleshoot the system with Nest Support, I had the white whire plugged into the aux terminal, but I hadn't yet identified that the one damper actuator was fried. They had suggested trying to plug the white cable into the * slot since the flow wasn't being controlled properly. I have ordered a replacement actuator and will rewire the thermostats back to the W2/Aux line.

With the white wire in Aux, the Nest thinks I have emergency heat. Is there additional configuration I need to do?

1
DrkMithNorCal Nest Pro•

Should be straightforward heatpump settup.....if the white is in * then it could be set as emergency heat, if it's in aux, then its auxiliary heat.

The nest will automatically control aux heat, but emergency heat is more a manual thing on the nest I belive

2
PewpasaurusOP•

Ok. I live in Florida, so I guess I had mistakenly assumed that auxiliary heat and duel fuel were kinda the same thing, so I was confused when I saw it.

1
DrkMithNorCal Nest Pro•

Dual fuel is if you have gas heat as a backup instead of electric backup, or a 2and heater as a backup heat source.

1