3 Question about Rim joist frosting/wet

The question are answered THANKS for the help.

my rim joist In my basement are frosting because of the cold air meeting the warm air. (No water leaks in the house and it hasn’t had any precipitation for about eight days. My question’s are:

would it be doing it in the walls?

And I was told to use rigid foam insulation and then use cans of diy spray foam to seal the rim joist will this work?

Wouldn’t my framing in the rim joist be having the same problem with the frost? (And if so is there anything I can do)

Posted Jan 24, 2020, 1:39 AM UTC · edited

55
BuildingSci•

Question 1 - Is there a possibility for wetting in the walls? Absolutely, but fortunately there should be significantly less warm wet air making its way into the wall than an exposed rim joist.

Question 2- The method you proposed is the easiest for a DIYer to complete. Make sure that you cut the foam as close to the same size as the joist bays and completely seal the edges of the foam to the framing.

Question 3 - Are you concerned about the joists coming out from the rim or the rim on a second floor?

3
JDP1982OP•

Thank so much first off. I don’t think I did the best job of writing question 3. Sorry for that.

But my concern is the actual framing. Mostly the rim joist part of the wood coming in contact with the actual framing.
I hope that explains it better

2
BuildingSci•

Once you prevent warm air from coming in contact with the rim. The likelihood of damage will drop significantly, as long as no bulk moisture is coming in from the outside.

2
Nehoteco•

Your walls have an air barrier (drywall/plaster) that is separating the warm moist air in your home from condensing on the cold framing. The rigid foam will effectively do the same thing, and with the relatively high R value of foam products keep that surface above the dew point.

3
JDP1982OP•

That’s great, I was worried. Thank you so much for the info

2