Visual Fault Locator + Single Mode Fiber issues
Hello,
I'm new to fiber and recently started to test my fibers with a Fluke VisiFault Visual Fault Locator. To my surprise nearly every strand of single mode has huge faults near the connectors. Even the brand new stuff that we had on the shelf for a few years fails this test. I don't have this problem on most of my Multimode patch cables.
Is it possible I am using too strong of a VFL for this kind of fiber?
Specs on the device say:
Output < 1.3 mW
Wavelength 630-670 nm
Class II laser product
Posted Oct 16, 2020, 6:29 PM UTC
This isn't atypical. Remember, the VFL is just for visually spotting an issue that you are looking for, not really for verifying that your fiber has no issues.
If you're just testing the jumpers themselves, you should really only need to scope the ends to make sure they're clean. For your fiber runs that have connectors in the middle (patch panels, etc.) you really should be using a certifier or OTDR to verify them, or at the very least looking at the receive level on the equipment on both sides.
We do now have scopes from Viavi to perform clean testing up to the IEC 61300-3-35 standard. This has been a very helpful tool, although we are quickly learning it is impossible to keep the fiber clean for more than a few moments at a time.
Thanks for the tip on VFL. I figured this was a good test for us to perform some some manufacturers provide this on the little fiber certificates on new jumpers. I am going through my piles of old fibers and trying to see how they compare. It doesnt take long to VFL but I fear I may have overvalued this feedback.
We do have Fluke DTX data testers with fiber modules for Loss Testing. However, the reference cables are now failing the IEC clean standard and some of them are falling apart from wear and tear. Replacing the Test Reference Cables is surprisingly expensive. I was hoping we could gain enough confidence between clean testing and VFL testing to postpone ordering new TRCs.