Bryant Plus 90 showing error code 31. Drain isn't clogged. Cooling fan does NOT spin easily.
Should I replace the inducer assembly? When turning the cooling fan it kind of clunks and does not spin freely. Furnace model number is 350mav048080f. Figures it's like 38 and raining outside with no heat!
Posted Apr 19, 2022, 4:26 AM UTC
113
Yeah, that's a failed inducer motor for sure. Those inducer motors fail all the time. That wheel should spin freely. That said, there are a number of issues I look for on these units; namely the potential for cracked heat exchangers. How old is the system?
I second this. MAV is on the heat exchanger high failure rate. It might be the cause of the inducer trouble. You cleaned the white box in the blower assembly I would assume?
I did, it was actually clogged a few years ago so that's the first thing I checked. When the thermostat calls for heat the motor tries to turn but doesn't move.
Some telltail signs heat exchanger fails on that generation of carrier brand: sight glass on burner warped/melted, water leaking unexpectedly near the blower motor area, offputting rotten egg smell near the exhaust outside, smokers yellow staining inside the pipe. But combustion analysis from tech is the best way. Sorry for putting a bit of fear into the motor not spinning well, but don’t want you to spend $500+ to have a bigger issue
Thankfully I have none of those signs.. I ordered a replacement assembly for about 300 that will be here tomorrow. I figure I'll swap it out and see if that does it, if not it's new furnace time
System is 20 years old. How would I check for a cracked heat exchanger?
You can pull the blower assembly and get a peak at them. That said, just replace the furnace. You got 20 yrs out of it and you'll just be chasing problems. Even if the heat exchangers aren't already gone, they'll fail soon. But given when this was built and the issues in manufacturing on this unit, don't throw good money at a bad problem.
Get a rheem/ruud or Trane/American Standard to replace it. Go for a 2 stage 80% furnace and sleep better at night knowing CO isn't going to keep you from waking up.
I ended up spending the 300 and replacing the diverter motor.. I may be throwing good money after bad but I figure if I get another season out of it for 300 I'm way ahead of the game.
Did you check carbon monoxide from the flue?