GFCI Failure - No power at load terminals
Power went out on our deck lights. I tested plugs tracing back toward the GFCI - which was powered and both receptacles tested good. I hit the test and reset buttons. Again both GFCI receptacles were hot, but outlets on the load side were cold.
Disassembled the can to expose the wiring and verified with test gear - no voltage across the load terminals while both GFCI receptacles had power.
Talked to two electrician pals, this kind of failure is a first for us.
Anybody else seen this?
*** problem solved *** internal solenoid: Thanks u/JustinMcSlappy