mitsubishi minisplit having lots of issues

About 6 months ago I had a mitsubishi minisplit/heat pump system installed. It's a 24k btu compressor/inverter with 3 air handlers inside. Since it was installed it's been nothing but trouble.

Within a few weeks it wasn't cooling nearly as well, and when I finally got a tech out he found a leak in the refrigerant line right at the compressor. A couple weeks later, I noticed another reduction in cooling capacity, got a tech out, and he found another leak in a different line where it terminated at the compressor. A month or two after that I noticed more reduction in cooling capacity plus an oily substance dripping out the bottom of the line cover on the biggest indoor air handler. Got a tech out, and it was a 3rd refrigerant leak.

Now that that 3rd leak was fixed, I'm noticing the following oddities about the system:

  1. The compressor is making a high pitched hissing sound when in cooling mode. Kind of like water running through old pipes in the wall.

  2. On a high heat/high humidity day, my spare bedroom just wouldn't dehumidify. Historically there's never been any water issues in that room, and the rest of the house was able to get down to about 50%rh for the same temperature while that room in particular was stuck upwards of 80%, even though it had been the only room running for most of the day.

  3. Flipping an air handler from cooling mode to fan mode will cause hot (measured around 90 degrees with a probe), extremely moist air to blow out for several minutes.

  4. There's an oily scuzz built up on the sides of all the condensate pump reservoirs underneath the air handlers. Is this indicative of more refrigerant leaks?

  5. Cooling capacity just seems all over the place. I'll swear an air handler just isn't cooling down even though it's the only one running, but when I measure it it will (eventually) get down to a 20 degree temperature differential between input and output air. Sometimes it takes upwards of 15-30 minutes though before it can get to that temperature though.

  6. Running in cooling mode, there's condensation all around the outdoor compressor. I'm also seeing water drips coming out of the joints of the indoor line covers.

I have a tech scheduled to come and look at it next week, so I guess my questions to you guys before he gets here are:

  • Are the weird things I'm seeing actual problems, or are they just psychosomatic because I've had so many other issues with the refrigerant leaks?

  • What questions should I have for the tech when he's out here? Is there anything I should make sure the tech looks at and/or addresses? e.g. every other time they've been out for the lack of cooling issues, they found a leak, went "yup that's it" and indicated that there was no need to check any other connections. Should I have been more firm about them testing all of the other connections before they called it fixed?

  • Is the amount of leaks I'm having "normal" or should I be looking for a different company to service this? It's still under the installers warranty and so I'm using their techs, it's just really annoying that I've had to have them out to look at it on average of once a month at this point. I really want this thing to work and work consistently.

Posted Sep 15, 2022, 6:10 PM UTC

217
Wonderful_City9340•

It seems to me like a poor installation

10
dpidcoeOP•

It seems to me like a poor installation

Right, but do you have any input as to what problems should I be leaning on the installer about and which things are just "working as intended"? Or is this a case where everything I described is an honest to god issue that I should be making them fix?

1
FuckBrendan•

I’m curious- do you have white insulation on your linesets?

1
dpidcoeOP•

It's a dark grey kind of insulation.

1
SharpAlfalfa8980•

Mitsubishi is really the standard for ductless. We’ve always had great success with them. Sounds like the installation company did a poor job through all this with the issues you’ve had

3
dpidcoeOP•

Mitsubishi is really the standard for ductless. We’ve always had great success with them.

That's what I've read online, and I have a friend who put in a mitsubishi system a couple of years ago and it's served him very well. It's even part of the reason why I picked this installer over a different one, because the other one was trying to install some no-name brand I'd never heard of before.

Sounds like the installation company did a poor job through all this with the issues you’ve had

So are you saying everything that I listed there is a legitimate complaint? I guess I'm mostly just looking for some reassurance that the issues I'm having are actual issues so that I don't start making demands only to find out that it's actually working as intended.

1
Silver_goboApproved Technician•

There’s a big concern with how they are refilling the system after they fix the leaks. Are they removing all the refrigerant, vacuuming the system out again, and adding fresh? Or do they just pump the refrigerant into the compressor and fix the leak, then top up with more refrigerant. Ductless systems have a far more narrow range of weight of the charge compared to traditional ACs… so it’s undetermined if the proper amount is in the system. There’s also concerns with the amount of leaks that have occurred moisture/contaminants have entered the system

1
dpidcoeOP•

Are they removing all the refrigerant, vacuuming the system out again, and adding fresh?

I think so. I heard a vacuum pump running while they were working on it, so I think they pumped everything out. I'd assume they also ran a pressure test and that's what gave them the confidence each time to just bug out without running their leak detector over the other head units.

1
Silver_goboApproved Technician•

How much have you paid them since the install??

1
flowerpower4life•

No not normal. Proper flared, aligned and torques joints with spec’ lineset copper don’t leak. Next time your spare bedroom is having trouble, shut off all other indoor units and see what happens. If it picks up performance in a big way, there is an issue with the circuit, could be low on refrigerant.

Best path forward is to find another company to give an opinion. Well worth what they’d charge.

3
dpidcoeOP•

Next time your spare bedroom is having trouble, shut off all other indoor units and see what happens. If it picks up performance in a big way, there is an issue with the circuit, could be low on refrigerant.

That's really helpful, thanks! The entire system definitely starts lagging if I have multiple indoor units running. I'd just assumed that was to be expected.

Best path forward is to find another company to give an opinion. Well worth what they’d charge.

I'm definitely leaning this direction. 80 bucks for a service call is a drop in the bucket compared to what I paid for the system.

1
motterpaul•

It almost sounds like they sold you a used system or something, that is an awful lot of problems. Questions: have you been using it for heat (raises the pressure a great deal), have you been moving the outdoor unit and is it securely mounted? Are the linesets properly insulated and tucked inside some kind of covering?

I would ask for an installer to recover all the coolant in the unit,

Do a nitrogen pressure test at a pretty high psi (especially if you use it for heat) and use soap bubbles and a sniffer to look for leaks all over.

Next: vacuum with a micron gauge, make sure it gets down well below 500 microns and does not return above 1000 (500 ideally) when the pump is removed.

Check the unit for its recommended load and also determine if you need to adjust that for longer line sets.

Make sure all the line sets a well insulated

Use fresh virgin R410a to reload the system. Check again for leaks.

1
dpidcoeOP•

Questions: have you been using it for heat (raises the pressure a great deal)

Aside from testing after each "repair", nope. This is san diego so I expect to use it for heat like once a year.

have you been moving the outdoor unit and is it securely mounted?

It's sitting on top of a plastic pad on my balcony with the lineset running indoors through where the old heater closet used to be. I don't think it's been moving. That said, how sensitive are these things to vibration? I'm near a navy airbase, and sometimes an osprey will do a low and slow pass with enough oomph at just the right frequency to vibrate the walls and set off car alarms.

Are the linesets properly insulated and tucked inside some kind of covering?

They're wrapped in insulation and behind a plastic lineset cover where they run outdoors on my balcony and also down from the ceiling indoors. A quick visual inspection shows me that it was slit lengthwise and cut back a little bit on some of the lines (presumably the lines where they were fixing leaks?).

Do a nitrogen pressure test at a pretty high psi (especially if you use it for heat) and use soap bubbles and a sniffer to look for leaks all over.

Next: vacuum with a micron gauge, make sure it gets down well below 500 microns and does not return above 1000 (500 ideally) when the pump is removed.

Check the unit for its recommended load and also determine if you need to adjust that for longer line sets.

Make sure all the line sets a well insulated

Use fresh virgin R410a to reload the system. Check again for leaks.

Aha perfect, now I know exactly what to ask the guy / make sure he does when he's out here next week. Thanks!

1
motterpaul•

It depends on how much vibration there is. If the unit is actually moving it can be enough to knock a flare loose. Makers generally recommend a cement pad instead of plastic.

I forgot to mention that they should also use a torque wrench and follow the manual for the recommended amount of tension when tightening all flares.

Also - bubble testing under nitrogen is very important, and so is a micron gauge when pulling a vacuum. Sadly, many DIY manuals skip these two factors, but a pro outfit should use them with every inspection.

1