Looking to install a NEMA 14/50. Is there any way to get around adding a sub panel?
reddit.com/gallery/112ko7vPosted Feb 15, 2023, 12:23 AM UTC
Posted Feb 15, 2023, 12:23 AM UTC
Tandem breakers.
That was my thought, but I can't tell if this panel can take tandem breakers from the wiring diagram.
A BD (listed on the label for your panel) is a tandem BR.
[deleted]
You have 200amps, don't need the dcc-12, good idea if it was only 100. Just get a quad 15-50-50-15 and remove two single 15s.
You could combine the kitchen and entry lights onto the same circuit. If the only thing on there is lights and likely no need for multiple circuits with led lights.
The easiest place to install a 14-50 receptacle is directly below the panel. You can install a surface mounted box or a flush box. If you install a flush box, you are going to have to attach it to the wall behind the box with some standoffs. A cut-in box will quickly break the drywall holding it due to the large amount of force required to insert a 14-50 plug.
If you’re talking breaker space, you can use tandems or a 20/50 quad. If you’re talking about amperage, a DCC-12 will work safely with your existing system. Hope this helps.
I wasn't sure if this panel could take tandem breakers or not based on the wiring diagram or if I was looking at installing a new sub panel. I really don't know if I'm ever going to install any more breakers so I was hoping I didn't need a sub panel.